IP addresses are NOT logged in this forum so there's no point asking. Please note that this forum is full of homophobes, racists, lunatics, schizophrenics & absolute nut jobs with a smattering of geniuses, Chinese chauvinists, Moderate Muslims and last but not least a couple of "know-it-alls" constantly sprouting their dubious wisdom. If you believe that content generated by unsavory characters might cause you offense PLEASE LEAVE NOW! Sammyboy Admin and Staff are not responsible for your hurt feelings should you choose to read any of the content here. The OTHER forum is HERE so please stop asking.
I need some help here. For a 2 element 3 phase 3 wire connections (AB and CB) where phase B is connected to neutral, would phase B display any voltage readings?
I need some help here. For a 2 element 3 phase 3 wire connections (AB and CB) where phase B is connected to neutral, would phase B display any voltage readings?
I need some help here. For a 2 element 3 phase 3 wire connections (AB and CB) where phase B is connected to neutral, would phase B display any voltage readings?
What u talking about ?
1. U want to use 3 phase as single phase? Just use of of the 3 phase and neutral
2. Or u want to joint direct phase to neutral? That will trip.
3. Or u want to know if 3 phase meter using one phase only for single power the appliance eg. fan? The electric meter will still run. Because electric meter calculate Kw total from all the 3 phase.
What u talking about ?
1. U want to use 3 phase as single phase? Just use of of the 3 phase and neutral
2. Or u want to joint direct phase to neutral? That will trip.
3. Or u want to know if 3 phase meter using one phase only for single power the appliance eg. fan? The electric meter will still run. Because electric meter calculate Kw total from all the 3 phase.
I need some help here. For a 2 element 3 phase 3 wire connections (AB and CB) where phase B is connected to neutral, would phase B display any voltage readings?
The presence of a voltage reading depends on your what your test probs are tabbing onto. i.e. your phase B in relation to what? Other phases or earth or what?
I need some help here. For a 2 element 3 phase 3 wire connections (AB and CB) where phase B is connected to neutral, would phase B display any voltage readings?
If you are not in North America, you will not have 110/220 divisions, and since 3 phase is usually out for domestic households, you will only have 110 or 220 VAC. So if either a 110 or 220 V network, yr neutral is zero. If you have a BT system, it may be 110V and phasor voltage 220V.